I was just wanting to run something by you guys. I have a church that had some serious ice dam issues this year. This is just a simple roof 40 feet wide by 40 feet up on each side, it is about a 3 1/2 to 4 in 12, it is plywood decking. When I tore this roof off several years ago, I could look down in some of the roof vent holes and see another roof down below several feet. It appears when they did the addition many years ago they just planted new roof structure over old roof without removing.

This year they had ice leaks on this roof. I went over and the entire roof was ice, now granted we had 3-4" of freezing rain. But when the melting started, water backed up under black paper and leaked in. I had used ice shield along edges but it backed up even higher than that and went up to second seam in decking, about 8'. The church now had me price removing entire roof and felt, installing Grace Ice shield on entire roof, then installing new shingles.

My question is...Have any of you done this? What are pros and cons?

We don't get ice that often but this year was terrible. Now everyone is worried about ice dams so I need to find a reasonable way to install a roof that is 100% ice dam proof. Talk to me northern climate guys.

Thanks!

March 28, 2011 at 7:51 p.m.

tinner666

Might have to go back to 'roofing' methods, as opposed to 'miracle cure' under lays. Before we had miracle cures, we shortened the courses. A 4" keyway gets less damage exposure than a 5" keyway. I did a few dimensional shingle 2/12's with Elks, at 4" exporuse, 6"+ Dutch-laps. Some are 10+ years old and often have 24"+ of snow.

Those reps can tell us that with the new underlay, there is no need to shorten exposure."The I&W will take care of it. Obviously, they fully expect lots of water under there.

In hurricane areas, we went to 4" or less exposure. The shingles didn't blow off though they had no seal strip. Take a folding rule and see how much deflection there is between 0" and 4", then, try 0" to 5". Try it at 3" for fun too.

March 27, 2011 at 8:32 a.m.

RandyB1986

Yeah Twill........after this winter I have come to the conclusion that 3' of I&W along the eaves is worthless. It really does zero good with ice dams since the first plywood seam is at 4'(and that is where the water enters)..........but I am glad you said it failed at even 9'. I have started telling my customers if they want I&W to go at least 2 rows high(6')........but after hearing you, maybe that won't work either.

March 26, 2011 at 9:10 a.m.

soldierboy

Twill59

Installed what 9'? I think that on airvents website it has a link to a great excel spreadsheet. Input what the attic space is and it will tell you exactly what ventilation systems to use. Yes, 36' of Ridgevent that has 18 NFA's is much better than 6 Box vents.

If you stick to the facts about ventilation and not opinions you will be much better off. Talk to the enginers that test this stuff. Talk to the Colleges that write articles about ventilation. I am sure that you will find the answer with the experts. Most of us on here are Roofing Experts yet still find the need to get knowlege from other Experts in our field. I have personally asked a few for opinions. That's the great thing about these forums. Can you post a few pics? That would help out tremendously.

Soldierboy

March 22, 2011 at 9:20 p.m.

RandyB1986

Thanks guys..

Soldierboy......there is nothing between the deck and the other roof structure below. When I look thru vent holes, I just see another shingled roof about 3 feet below. Big time fire hazard......

AEI.....In your opinion is 36 feet of ridge vent better than 6 box vents? Soffits are aluminum and have about every other one vented.

I have not heard back on this job......still pondering what to do. My supplier also stopped carrying Grace Select, they only have the heavy Grace.

March 22, 2011 at 7:56 p.m.

AEIRoofing

If you install full ice shield manufacturers require "double the ventilation.

March 7, 2011 at 9:26 p.m.

soldierboy

From what Air vent states on the snow zone. Snow is porous and is breathable. The right insulation and ventilation is key to preventing ice dams. However, a $65.00 roof rake and a maintenance fee to remove the snow 3-4' up every time it snows will work 100% of the time. I have seen ice and water shield on entire homes and seen the misery it has caused that homeowner. If you do this you would have to make sure; as stated above to vent, vent, vent some more our you'll be replacing the decking. What else is in between this deck and the roof below it? Where did they stick their furnace? I have a Dr. office that has their furnace in the attic on top of an old flat roof below a 15 year old pitched roof. They get horrible ice dams and he has us clear them 3-4 times a year. He is fully vented but with that furnace up there he creates his own problems. Just my two cents worth :lol:

March 5, 2011 at 8:22 p.m.

TomB

Sooooo, does that mean if your not installing I&W to the ENTIE deck, there's no concern for adequate venting?....JK, a little ribbing there, for the MOTO stmnt....

Here's an interstng little tid-bit to ponder....There are particualr regions/areas up here that roofs hold FEET of snow throughout the winter & into spring....The ridge vent is useless at least half the year....

March 5, 2011 at 5:32 a.m.

Tarco Technical

Whereas some building codes and local jurisdictions prohibit direct adhesion to the deck, most do not explicitly state their position in this regard. Individual manufacturers have allowed or limited such applications. Nevertheless, when installing self-adhesive membranes to the ENTIRE deck, it is necessary to allow for sufficient ventilation.

February 28, 2011 at 9:15 p.m.

TomB

100%I&W is standard procedure here in the Colorado mountains....It's not required by any local bldg. codes. Nor is it the correct way in a lot of cases....It's just the way they roll....If you don't; Eyebrows begin to rise....Personally, I feel it came about to mask inferior workmanship.

We run into "I told you so" situations all the time. The ice daming dynamics change significantly when you take a 25 yr. old shake roof with no I&W what-so-ever, or adequate attic venting & seal'er all up with I&W & comp, all kinds of crazy stuff starts happening....We're surrounded by idiots...However, "when in Rome".....

February 28, 2011 at 11:20 a.m.

ottawa_roofer

Randy,you said you could see a seconday roof underneith. There should not be heat generated, it should be a cold spot.Installing Grace 100 % could cause "back up" on a heated roof. Seeing that it is not, it shouldn't be a prblem. Yes i've installed ice and water shield 100% on decks of that pitch,as long as you vent it over kill. vent, vent, vent. to keep it a cold spot, you don't want heat.

February 24, 2011 at 6:54 p.m.

dougger222

There have been quite a few insurance adjusters going around giving home owners new roofs this Winter with leaky ice dams.

What they should really do is give them a credit to use for an insulation/ventilation pro to fix the problem.

Got tons of calls from home owners with roofs ranging from 3 months to 2 years old with proper ice and water shield with leaks from ice dams this Winter.

Just so you know and keep this in mind when trouble shooting a new roof to a customer with ice dam issues. No manufacturer of ice and water shield will warrant against water back up on an ice dam causing a leak. They'll warrant wind driven rain and even ice but not standing water on an ice dam, plain and simple.

This Winter the biggest "puddle" I saw on a roof was about 6 inches deep. It was on a 3/12 with full ice and water. Yes, it found a way in!!

February 23, 2011 at 8:44 a.m.

RandyB1986

This building has good ventilation but insulation is a little low. This building don't usually ice up from snow.....it is just this year we had an ice storm followed by zero temps.....I bet 25% or more of homes had leaks.

What do you guys think about putting ice shield over felt paper? That way if it is ever torn off and replaced, the ice shield will come up and leave decking undamaged.

My main concern was sealing deck that tight.....but it sounds like others do it. I just don't want to leave any chance of another ice dam leak, it makes me look bad.

Thanks guys!

February 22, 2011 at 5:43 p.m.

copperman

You should look at correcting the insulation and vent problems first. I'm against ice & water shield on the whole deck. Would be a real dog to replace.


« Back To Roofers Talk
You must be logged in to reply to this topic.

Central States - Banner Ad - Expand your Business with Siding
English
English
Español
Français

User Access


Imperfelx Ads - Bitec 250x265 (1).jpg
Malco Tools - Sidebar Ad - Metal Benders
Equipter - Sidebar Ad - Drive. Lift. Dump. Repeat.
gFour Marketing - Sidebar Ad - Referrals
USG - Sidebar - Impact
Dataforma - Sidebar - Project Management
Roof Hugger - Sidebar - Q1