Find leaks / Water Testing Procedures ?

« Back To Roofers Talk
Author
Posts
August 3, 2009 at 4:58 p.m.

anotherguy

Please share with me. How should a shingle roof be tested during dry weather. Desert region: Shingle roof, 2:12 two plies 15# felt.

Does one just set a water hose on the roof and let it run? Moving it as needed to test different area's? Or. Do you put a sprinkler on the roof allowing the water to fall as rain would? What is the problem with moving a running hose from one are to another allowing it to run on the roof?>>>

August 8, 2009 at 4:31 p.m.

CIAK

Miscreant Said: Im really a roofer. I really am licensed to roof. Ive really been to college. Im not really a dog. These are four statements you could not truthfully make.

CIAK, there are either chemicals in your brain that shouldnt be there or some that should.

False and fraudulent accusations Miscreant . Throwing yourself to the dogs in lot with small minded grey gnats " Birds of a feather " " Romeo and Juliet ". Perhaps a meditation would clear the clouds from the mind . I was suspect you were better than than that . I believe you are . I'm still holding out you will come to your senses . I'll except your apology when you wake up from you slumber . Tch , Tch a little research will prove you embarrassingly wrong .>>>

August 8, 2009 at 2:55 p.m.

Miscreant

I'm really a roofer. I really am licensed to roof. I've really been to college. I'm not really a dog. These are four statements you could not truthfully make.

CIAK, there are either chemicals in your brain that shouldn't be there or some that should.>>>

August 8, 2009 at 9:42 a.m.

CIAK

Measure for Measure Miscreant, This sounds Polish to me .

Ty ani ciepła, uczucia, kończyn, ani piękna Aby twoje bogactwa przyjemne. Google for lanuage tools ;) ;) A hint I know it's Polish to you too . :laugh: :laugh: What a tool !!!!!!! :laugh: :laugh: :laugh: B) B) My question back to you Miscreant , quamdiu etiam furor iste tuus nos eludet? quem ad finem sese effrenata iactabit audacia? I won't try to hide behind a mask of congeniality . I'll translate for you ..........."For how long will that madness of yours mock us? To what end will your unbridled effrontery toss itself about?" I'm being attacked here by a stupid dog with sunglasses of all things . I'm willing to let it rest . I'll let the dogs have the table scraps . B) B) . I admitted to taking something a little to far . I was right in my assessment of Jets comment . End of story. I'm moving on.>>>

August 7, 2009 at 2:40 p.m.

Miscreant

What is mayacopa? You don't mean mea culpa. do you?

I suggest getting English anchored down before you tackle Latin.

Quo usque tandem abutere patientia nostra?

.>>>

August 7, 2009 at 11:53 a.m.

JET

IMO the main reason we come here is to discuss roofing issues, not argue. Some of the posters (one in particular) here don't have a REAL job so the only thing they can offer is attitude which has gotten very old over the past few months. I always consider the source.

JET>>>

August 7, 2009 at 6:21 a.m.

CIAK

Yeah pgriz your right I aplogize to all the RCS'ers. I deleted that last reply. mayacopa mayacopa .Thanks Paul . I admit I got out there. Jets a good fellow . B) ;) ;) :laugh:>>>

August 6, 2009 at 7:54 p.m.

pgriz

:angry: :S Ok, guys, this pissin contest can stop. Declare yourselves winners, losers, whatever, but this back and forth isn't winning friends and influencing people. So... can... we... move... on? :(>>>

August 6, 2009 at 11:09 a.m.

JET

CIAK Said:
JET Said:
craftesman Said: what are shingles doing on a 2-12 in the first place??????

Ditto.......shingle roofs under 4/12 pitch have no warranty from the mfg. without a peel and stick membrane covering the wood deck. Tear off and replace with single-ply membrane.

JET

And your point Jet ??? 6. LOW SLOPE APPLICATION On pitches 2 in. per foot to 4 in. per foot cover the deck with two layers of asphalt saturated felt. Begin by applying the felt in a 19 in. wide strip along the eaves and overhanging the drip edge by 1/4 to 3/4 in. Place a full 36 in. wide sheet over the 19 in. wide starter piece, completely overlapping it. All succeeding courses will be positioned to overlap the preceding course by 19 in. If winter temperatures average 25°F or less, thoroughly cement the felts to each other with TAM-PRO or TAMKO Plastic Roof Cement from eaves and rakes to a point of a least 24 in. inside the interior wall line of the building.

You didn't finish the paragraph.........."TAMKO's Moisture Grard Plus self-adhering waterproofing underlayment may be used in lieu of the cemented felts"

I guess my "point" is that no shingle roofer I've seen does anything NEAR this requirement for low slope shingle applications. When the roof fails.....and it will, the roofer (if he's still in business) will direct the customer to the mfg. for a solution.

JET>>>

August 6, 2009 at 10:42 a.m.

CIAK

JET Said:
craftesman Said: what are shingles doing on a 2-12 in the first place??????

Ditto.......shingle roofs under 4/12 pitch have no warranty from the mfg. without a peel and stick membrane covering the wood deck. Tear off and replace with single-ply membrane.

JET

And your point Jet ??? 6. LOW SLOPE APPLICATION On pitches 2 in. per foot to 4 in. per foot cover the deck with two layers of asphalt saturated felt. Begin by applying the felt in a 19 in. wide strip along the eaves and overhanging the drip edge by 1/4 to 3/4 in. Place a full 36 in. wide sheet over the 19 in. wide starter piece, completely overlapping it. All succeeding courses will be positioned to overlap the preceding course by 19 in. If winter temperatures average 25°F or less, thoroughly cement the felts to each other with TAM-PRO or TAMKO Plastic Roof Cement from eaves and rakes to a point of a least 24 in. inside the interior wall line of the building.>>>

August 6, 2009 at 9:54 a.m.

JET

CIAK Said: Jet I Missed that in the manufacture warranty . Im still looking and it would be helpful if you could reply with where that is in the manufacture warranty. Stated in writhing by the manufacture. S/A felts though they look like a great product have not faced the test of real life climate conditions. They havent been around that long to really test them IMO

Jeez.......mister "go to here" can't find the goods now? Try this place, www.tamko.com and look under the "Roof Deck". Then go over to No. 6 "Low Slope Application". Hope this clears it up for 'ya.......

JET>>>

August 6, 2009 at 6:54 a.m.

CIAK

I have found that H/O's will decide their roofing decision based on budget, the number of years they plan to live in the house, around here how long they plan on living period the climate and the design of their house . I'm still challenging Jet to show where in the manufacture warranty he can substantiate his claim . I'm willing to admit I'm wrong if it can be shown to me . Come on Jet cough it up " ole pal . " ;) ;) B)>>>

August 5, 2009 at 8:10 p.m.

CIAK

It is not a requirement here either. A lot of guys sell it that is for sure . It didn't really start to pick up steam till a couple years back when there was a real paranoia about second water barriers. 30 is an accepted product for the second water barrier here in my county. Just more from my ole pal Jet . He may have inhaled to many stoogies . S/A may be a good idea not a requirement. Unless someone can show me otherwise. That is the challenge. Where is that requirement and where is the manufacture non- warranty statements ?>>>

August 5, 2009 at 5:16 p.m.

egg

We've run into situations like this before on this board.

1. Some regional areas have specifications that trump all others. Florida is the kind of place where that type of trump is as likely to occur as any. Florida guys have a decided tendency to assume whatever is required in their state is some kind of universal law applicable to everywhere else in the roofing plane of existence. With all due respect, this is not the case.

2. It is not a matter of conjecture; manufacturers of most if not all shingles available to me ALLOW and warrantee their shingles on applications for pitches down to 2/12. Nothing more need be said. It is just a fact. IN GENERAL, without intending to oversimplify, code defers to manufacturer specs for application and therefore, in general, manuf. specs become de facto CODE.

3. Applying shingles at that pitch is not the best idea, but I have roofs of long-standing service that are irrefutable proof that it works. Let me just emphasize: IN MY CLIMATE ZONE. I would be extremely reluctant to push any limits when ice dams are a factor.

4. The guy, going by the moniker of 'anotherguy', is in a "Desert region." (Hello????)

5. Don't you just love it when somebody poses something on the forum and then neglects to come back and respond to any of the replies?

6. This is important. Where I work, we have to have a Class A fire rating on all roof coverings. At 2/12 you don't get that with mineral surface cap sheets without having to go to extra lengths. You cannot mop down or torch down your same old favorite deal and meet that Class A requirement at that pitch. 2/12 to 4/12 (in fact, .5/12 to 4/12) is a very strange zone, let me tell you. Sermon ended.>>>

August 5, 2009 at 4:52 p.m.

CIAK

tinner666 Said: I reread the original question. My earlier response was based on my reading it as 2 plies of shingles. Still, shingles on 2/12 over 2 plies of 15 felt arent going to fare well either.

[/quote 2/12 over 2 plies of 15 was the norm around here for 3-4 maybe more decades and still continues today . It is a proven system that has functioned in a properly installed roofing system . If the system is installed properly no leaks for 20 - 25 yrs . There may be some maintenance a tab blown off here and there . I have used the S/A' s I want Jet to back up his " no " Manufacture warranty issue . Pretty simple . I'm suspicious the S/A's are used to cover up otherwise poor workmanship.>>>

August 5, 2009 at 4:34 p.m.

tinner666

I reread the original question. My earlier response was based on my reading it as 2 plies of shingles. Still, shingles on 2/12 over 2 plies of 15 felt aren't going to fare well either.

>>>


« Back To Roofers Talk
You must be logged in to reply to this topic.

English
English
Español
Français

User Access


Glo Group - LDR Accelerator - Sidebar
RCS - Sidebar Ad - 2025 Trends Survey
RCS - Sidebar - L&L contest
Pli-Dek - Sidebar - Only the Best - June
WSRCA - Sidebar Ad - WRE 2025_04.24.2025
Sales Assist - Sidebar Ad - Build Present Close
SRS - Sidebar Ad (En Espanol Page) - Roof Hub