Temporary Roof Failure

« Back To Observations from the Field
Author
Posts
May 27, 2025 at 3:49 p.m.

HannahFord7

Issue: The roofing contractor was unable to complete the roofing section in progress before the end of the workday.  The installed insulation was temporarily covered with tarps for the night.  Rain and wind occurred that night, blowing off the tarps and soaking the insulation.

May 27, 2025 at 3:51 p.m.

HannahFord7

According to Benchmark: 

Solution: Benchmark was retained to perform part-time observation and was not on site the prior day.  The Benchmark field consultant arrived the next morning and found the contractor ready to install membrane over the wet insulation.  The installation was stopped, and the contractor was advised to remove and dispose of the wet insulation prior to continuing.  The field consultant worked with the roofing contractor to establish the area of roof that could be accomplished each day and completely covered with roofing membrane in a permanent watertight condition.

Possible Impact: Installing membrane over wet insulation would have resulted in trapped moisture within the new roof system, poor adhesion of the membrane, and corrosion of the metal deck.  Investing in project observation by Benchmark ensured that the Owner avoided future issues with their roof due to poor workmanship and shortcuts by the Contractor.


« Back To Observations from the Field
You must be logged in to reply to this topic.

APOC - Banner - Tuff Grip
English
English
Español
Français

User Access


Sign up for Week in Outdoors eNews!
RCS -  - L&L contest
AskARoofer -  Ad - AAR Podcasts
OCS - OutdoorCoffeeShop
Pli-Dek -  - Only the Best - June
Anchor Products -  Ad - Newsletter April
Equipter - Financing -